Jump to content
Did you know?
  • The original Rudolph did not have a red nose. In that day and age, red noses were seen as an indicator of chronic alcoholism and Montgomery Ward didn’t want him to look like a drunkard. To complete the original picture, he was almost named Reginald or Rollo.
  • The Christmas wreath was originally hung as a symbol of Jesus. The holly represents his crown of thorns and the red berries the blood he shed.
  • The three traditional colors of most Christmas decorations are red, green and gold. Red symbolizes the blood of Christ, green symbolized life and rebirth, and gold represents light, royalty and wealth.
  • Tinsel was invented in 1610 in Germany and was once made of real silver.
  • The oldest artificial Christmas trees date back to the late 1800s and were made of green raffia (think grass hula skirts) or dyed goose feathers. Next the Addis Brush Company used their machinery that wove toilet brushes to create pine-like branches for artificial Christmas trees that were less flammable and could hold heavier decorations.
  • ‘Jingle Bells’ – the popular Christmas song was composed by James Pierpont in Massachusetts, America. It was, however, written for thanksgiving and not Christmas.
  • Coca-Cola was the first company that used Santa Claus during the winter season for promotion.
  • Hallmark introduced their first Christmas cards in 1915.
  • The first recorded date of Christmas being celebrated on December 25th was in 336, during the time of the Roman Emperor Constantine. A few years later, Pope Julius I officially declared that the birth of Jesus would be celebrated on that day.
  • Santa Claus's sleigh is led by eight reindeer: Dasher, Dancer, Prancer, Vixen, Comet, Cupid, Dunder (variously spelled Donder and Donner), and Blixem (variously spelled Blixen and Blitzen), with Rudolph being a 20th-century inclusion.
  • Outdoor Christmas lights on homes evolved from decorating the traditional Christmas tree and house with candles during the Christmas season. Lighting the tree with small candles dates back to the 17th century and originated in Germany before spreading to Eastern Europe.
  • That big, jolly man in the red suit with a white beard didn’t always look that way. Prior to 1931, Santa was depicted as everything from a tall gaunt man to a spooky-looking elf. He has donned a bishop's robe and a Norse huntsman's animal skin. When Civil War cartoonist Thomas Nast drew Santa Claus for Harper's Weekly in 1862, Santa was a small elflike figure who supported the Union. Nast continued to draw Santa for 30 years, changing the color of his coat from tan to the red he’s known for today.
  • Christmas 2018 countdown has already begun. Will you be ready???
  • Why do we love Christmas? It's all about the traditions. In this chaotic world we can miss the "good old days." Christmas reminds us of that time.
Mark Clements

Breaker getting hot

Recommended Posts

I finished my display today I have put up more this year then any year before .I took a bunch of amp readings I was pulling 115 amps 58 amps on A phase and 57 on B phase . I have 11 20 amp circuits the most on any circuit is 15 amps so I have it well balanced. Well this evening I smelled something getting hot I went downstairs to my main panel and my 100 amp breaker that feeds my sub panel in the garage was hot . I went to my garage panel and my main breaker on it was fine. I shut my display down for the night and tomorrow I will have to get a new 100 amp breaker for my panel . I am going to move the breaker up in my panel closer to my main 200 amp breaker which should help with the heat I will know more tomorrow when I pull the breaker out .I guess the moral of the story is keep a close eye out for your breakers getting hot . I thought I had done everything right but it still got hot I think my100 amp breaker is old . I just hope I haven't hurt my panel I would hat to not be able to run my display when I just finished it but I would hate more burning my house down lol wish me luck tomorrow.

Share this post


Link to post
Share on other sites

It Normal for your breaker to warm, putting it closer to the 200A breaker will make it worse, try to keep it from other so it can dispate the heat. You may have a bad breaker, but don't be suprised if the new breaker gets warm also. If its so hot you can't keep your hand on it then yes there some thing wrong, check to see that all your connection are tight, even at the main panel. One loose wire and it can cause a lot of heat.

Share this post


Link to post
Share on other sites

If the loading is as you say then the breaker should not have been hot regardless of position within the panel. What is more likely the culprit is that the breaker stabs that go over the bus bar in the panel have loosened over time and this loose connection will heat up. This is how the great majority of panel failures and fires occur.

Tony

Share this post


Link to post
Share on other sites

My thinking on moving the breaker up is on my panel the bus is split on bottom so you can add tandem breakers on top by the main it isn't so should get a better connection . Tony I think you are right the breaker is the problem

Share this post


Link to post
Share on other sites

I put the new breaker in I took some amp readings now I am only drawing 45 amps on A phase and 40 on B phase so that breaker heating up was causeing higher amps . here are two pics one is upc labels from brakers right across from 100 amp breaker the other of my panel you can see on the top left my bus is discolered .

PB280858.jpg

PB280860.jpg

Share this post


Link to post
Share on other sites

Mark,

You really want to move that breaker and not use those two slots again, don't forget to get snap-in fillers for the panel cover. Once those bus stabs have been heated that severely getting them to be reliable again will be a challenge. My biggest concern is that most residential panelboards have aluminum bus bars in them and aluminum does not do well after it has been overheated. The metal weakens due to fatigue and the overheating and then cooling off. Depeding on the overall condition of the bus you may be looking at a panel replacement.

Tony

Share this post


Link to post
Share on other sites

Mark,

You really want to move that breaker and not use those two slots again, don't forget to get snap-in fillers for the panel cover. Once those bus stabs have been heated that severely getting them to be reliable again will be a challenge. My biggest concern is that most residential panelboards have aluminum bus bars in them and aluminum does not do well after it has been overheated. The metal weakens due to fatigue and the overheating and then cooling off. Depeding on the overall condition of the bus you may be looking at a panel replacement.

Tony

Tony I moved the breaker all the way up top and I wont use that spot again I still have lots of free space in panel . Bus still looks in good shape except in that one spot I will keep a close eye on it if I notice anything I will replace panel and get a better one next time .My garage panel is a bolt in it is much nicer then my main panel . I had DOH moment when I said my amp draw had went down I had forgotten I had turned off my two highest amp breakers of in my sub panel but new breaker is doing well and not getting hot so far so good Thanks for the advise

Share this post


Link to post
Share on other sites

I am happy to report my new breaker preformed great tonight didn't even get warm I feel much better . I was afraid I was going to have to take quite a few things down .

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest